Drainage - Foul drainage on a 1:5 slope
-
- Posts: 1
- Joined: Tue Nov 19, 2019 4:27 pm
- Location: Oundle
-
- Site Admin
- Posts: 8346
- Joined: Mon Jul 05, 2004 7:27 pm
- Location: Warrington, People's Republic of South Lancashire
- Contact:
That's relatively steep, but not to the point of being ridiculous.
You can lay at 1:5, if you wish, but the alternative would be to lay the pipe at, say, 1:20 or thereabouts, and then use a drop shaft connection where it meets the existing... Dropshaft Connection
Personally, I prefer dropshafts as they keep the flow rate sensible and they reduce the amount of excavation required.
You can lay at 1:5, if you wish, but the alternative would be to lay the pipe at, say, 1:20 or thereabouts, and then use a drop shaft connection where it meets the existing... Dropshaft Connection
Personally, I prefer dropshafts as they keep the flow rate sensible and they reduce the amount of excavation required.