I will be bolting down a large number of 8mm thick Galvanised base
plates onto a reinforced concrete raft.
The plates are 300 x 300 and each fixed by 4 M16 anchor bolts - picture of thems at:
http://tinyurl.com/2qdjlj
The plates while pretty darn good, are not perfectly flat ... the welding on the upper faces (300 high T section in 8mm steel) plus in places the concrete may be a couple of mm out, although it is a good powerfloat finish.
We are only talking about slight rocking of the base plates, and the torquing each of the bolts to 100 lb ft will probably pull bases flat.
These are being used externally and will be subject to wet & full UK temp range. (hence the galv)
I have thought about spacing the plates up off the slab using 10mm packers, and then arranging a small formwork around the base plate, and pour in cementitious grout. (Cemgrout EF?)
The sequence I will follow then would be ..
Drill holes
Shim plates with 10mm steel spacers
Fine adjust to get plates plumb
Torque to 75% on finished setting
Create formwork, giving aprox 20mm all round base plate.
Pour cementitious grout
Let it set for specified time (24 hrs = 30 N/mm2)
Torque down bolts to final 100 lb ft
Does the above all sounds logical ?
The only issue I can think of .... the grout will be poured and will surround anchors & bolts threads .. when I then go to give final torque ... will the threads turn with no problem ? or conversely will turning them cause a problem.
Do I need to consider this ? .....pre-treat threads in any way ? or even perhaps look at full torquing down (onto shims) before grout is poured.
Thanks for any advice on this.
plates onto a reinforced concrete raft.
The plates are 300 x 300 and each fixed by 4 M16 anchor bolts - picture of thems at:
http://tinyurl.com/2qdjlj
The plates while pretty darn good, are not perfectly flat ... the welding on the upper faces (300 high T section in 8mm steel) plus in places the concrete may be a couple of mm out, although it is a good powerfloat finish.
We are only talking about slight rocking of the base plates, and the torquing each of the bolts to 100 lb ft will probably pull bases flat.
These are being used externally and will be subject to wet & full UK temp range. (hence the galv)
I have thought about spacing the plates up off the slab using 10mm packers, and then arranging a small formwork around the base plate, and pour in cementitious grout. (Cemgrout EF?)
The sequence I will follow then would be ..
Drill holes
Shim plates with 10mm steel spacers
Fine adjust to get plates plumb
Torque to 75% on finished setting
Create formwork, giving aprox 20mm all round base plate.
Pour cementitious grout
Let it set for specified time (24 hrs = 30 N/mm2)
Torque down bolts to final 100 lb ft
Does the above all sounds logical ?
The only issue I can think of .... the grout will be poured and will surround anchors & bolts threads .. when I then go to give final torque ... will the threads turn with no problem ? or conversely will turning them cause a problem.
Do I need to consider this ? .....pre-treat threads in any way ? or even perhaps look at full torquing down (onto shims) before grout is poured.
Thanks for any advice on this.