Necessary pipe diameter to drain per square metre
-
- Posts: 45
- Joined: Sat Nov 15, 2014 4:38 pm
- Location: Uk
This should possibly of been an earlier question I asked but,
Are there regulations specifying the drain capabilities of a pipe in relation to the area it hopes to drain.
I plan to drain an area that could catch approx 180m2 of rainfall into a 110mm pipe.
Calculation is belt and braces and a!lows for next doors rainfall into shared roof downpipe and probably some/most of there rainwater at ground level. Ideally neighbour would divert their own rain but sadly a fair bit of there's will run into my garden and I would rather it went down a pipe than have standing water.
Hopefully I have worded this soyou guys can understand.
Thanks
Are there regulations specifying the drain capabilities of a pipe in relation to the area it hopes to drain.
I plan to drain an area that could catch approx 180m2 of rainfall into a 110mm pipe.
Calculation is belt and braces and a!lows for next doors rainfall into shared roof downpipe and probably some/most of there rainwater at ground level. Ideally neighbour would divert their own rain but sadly a fair bit of there's will run into my garden and I would rather it went down a pipe than have standing water.
Hopefully I have worded this soyou guys can understand.
Thanks
Thank-you for helping.
-
- Site Admin
- Posts: 4713
- Joined: Mon Jun 26, 2006 11:01 am
- Location: eastbourne
-
- Posts: 45
- Joined: Sat Nov 15, 2014 4:38 pm
- Location: Uk
Thanks for taking the time help sean and ruby.
Will connect to same outlet as guttering downpipes (storm)
Ideally neighbours would deal with they're rainwater but I can't see them lifting they're slabs to stop they're water running under fence and into our slabs. So rather than encouraging standing watervi think it best to deal with it head on. Both houses have a very small strip of garden chips beside house (garden slopes towards house) to give drainage but from what I've reads strip of chips isn't the greatest drainage system. Think its possible for me to lift and relay some slabs to make a "bowl" with a gully pot at centre to take away water.
Just hoping a 110mm has a high enough capacity for my needs.
My 180m2 calculation is based on two back garden and two roofs on the same side all draining to same outlet.
Thanks
Will connect to same outlet as guttering downpipes (storm)
Ideally neighbours would deal with they're rainwater but I can't see them lifting they're slabs to stop they're water running under fence and into our slabs. So rather than encouraging standing watervi think it best to deal with it head on. Both houses have a very small strip of garden chips beside house (garden slopes towards house) to give drainage but from what I've reads strip of chips isn't the greatest drainage system. Think its possible for me to lift and relay some slabs to make a "bowl" with a gully pot at centre to take away water.
Just hoping a 110mm has a high enough capacity for my needs.
My 180m2 calculation is based on two back garden and two roofs on the same side all draining to same outlet.
Thanks
Thank-you for helping.
-
- Site Admin
- Posts: 4713
- Joined: Mon Jun 26, 2006 11:01 am
- Location: eastbourne
-
- Site Admin
- Posts: 8346
- Joined: Mon Jul 05, 2004 7:27 pm
- Location: Warrington, People's Republic of South Lancashire
- Contact:
In theory, you should be able to effectively 'drain' 300m² vis a 100/110mm dia pipe, but that's it ruynning at ful bore and assumes there are no obstructions to the flow. This values is based on the 1-in-25 year storm rate.
However, if this 100/110mm pipe connects into, say, an IC with two other lines coming in, and each of them is 100/110mm, with an 100/110mm outlet, then there is a big problem. There is real potential for water to come into the IC faster than it can escape, and so the chamber will surcharge (overflow).
In such a situation, we'd look to use an outlet of 150mm or larger so that, during this hypothetical once-in-25 year event, there's no risk of surcharging.
Coming back to your situation, I'd be happier relying on 150mm dia pipework for an area of 180m², but just where is all that water going to go?
However, if this 100/110mm pipe connects into, say, an IC with two other lines coming in, and each of them is 100/110mm, with an 100/110mm outlet, then there is a big problem. There is real potential for water to come into the IC faster than it can escape, and so the chamber will surcharge (overflow).
In such a situation, we'd look to use an outlet of 150mm or larger so that, during this hypothetical once-in-25 year event, there's no risk of surcharging.
Coming back to your situation, I'd be happier relying on 150mm dia pipework for an area of 180m², but just where is all that water going to go?
Site Agent - Pavingexpert
-
- Posts: 45
- Joined: Sat Nov 15, 2014 4:38 pm
- Location: Uk
OK,
Two 68mm pipes connecting into approx 4 inch pipe as outlet.
Draining approx 180m2 from roofs and ground level?
I've done some exploratory digging and have made necessary connections, just need to install and connect gully pot. I'm confident that will have sufficient fall on it.
Just hope someone in the know can confirm its up to standard???
Two 68mm pipes connecting into approx 4 inch pipe as outlet.
Draining approx 180m2 from roofs and ground level?
I've done some exploratory digging and have made necessary connections, just need to install and connect gully pot. I'm confident that will have sufficient fall on it.
Just hope someone in the know can confirm its up to standard???
Thank-you for helping.
-
- Site Admin
- Posts: 4732
- Joined: Fri Jul 28, 2006 8:47 pm
- Location: Somerset
- Contact:
110mm will be fine