Suds system - Workaround for shallow drains?

Foul and surface water, private drains and public sewers, land drains and soakaways, filter drains and any other ways of getting rid of water.
Post Reply
Sync700uk
Posts: 1
Joined: Fri May 26, 2006 5:45 pm
Location: lancashire

Post: # 12174Post Sync700uk

Firstly,congratulations on the single most informative website of it's type that I have come across. I've learnt how much I do not know :)

I have a problem of shallow main drains and problematic building constraints from 'She Who Must Be Obeyed'.

I'm looking to provide surface and groundwater drainage for the reworking of a patio area . The ground is heavy clay, prone to flooding and slopes towards the house. The only viable outlet is the main SW drain.

I was planning a simple system of flexi land pipes ultimately connecting to the SW drain with an adapter. On excavation, I find the main drain to be 4 - 5 courses below DPC (say 350- 400 mm) . However existng ground level is only 3 courses below DPC,( say 200 mm). I don't see how I can sink a land drain far enough below ground level for it to be structually sound and functionally effective even using reduced minimum depths :(

The Linear drains attracted a frown from SWMBO and the same has expressed a wish for 'no little steps' in her patio area so raising the patio is not an option either. I have doubts whether the 'bodged job' tactic of gravel/stones against the brick wall would give us the drainage power needed. On a brighter note, SWMBO wants gravel between the pavers. This opens up SUDS :cool

The terram drainage composites are nice but way too expensive in horizontal use. However, I did track down a website promoting a Terram product called 'Advantage'. It says it is used for drainage, including wrapped drains but I can't determine whether this product can be use as a horizontal drainage composite membrane. The question therefore has three parts. ???

1/ Can I use the 'suds solution for a patio' you've outlined in the SUDS pages where the drainage trench will be up against the house?

2/ Do you think I could use the terran advantage membrane as a horizontal composite linking into it. This is the website
Terram advantage

3/ By my calculations the the drainage trench will only be about 225 mm below the cobbles/pebbles on the surface in order for pavers not to exceed DPC and a sufficent fall to exist from the bottom of the trench to the SW drain connection. Can I get away with that?

Any advice much appreciated :blues:
Adrian Maudsley

Tony McC
Site Admin
Posts: 8346
Joined: Mon Jul 05, 2004 7:27 pm
Location: Warrington, People's Republic of South Lancashire
Contact:

Post: # 12274Post Tony McC

1 - SUDS is probably not going to be all that easy on a site you say is prone to waterlogging. It all depends on the percolation rate for your sub-grade.

2 - Terram Advantage is simply a 'general purpose' geotextile. It is NOT a composite, so it won't work as you imagine as a horizontal drain.

3 - This goes back to Q1. I think your best option is likely to be a linear channel of some description.
Site Agent - Pavingexpert