Just wondering whether there is a standard for access on long drain runs for SW. I know foul has to have a manhole at least every 90m, is it the same for SW?

Cheers in advance

Rik

(Edited by Rik at 6:40 pm on April 26, 2003)

84-1093879891

Post: # 1738Post 84-1093879891

The standards are the same for FW and for SW. 90m is the max spacing for Manholes - IC's or access chambers (as used on residential drainage) have a lesser maximum separation distance (45m)

Rik
Posts: 2
Joined: Sat Apr 26, 2003 6:22 pm

Post: # 1745Post Rik

Many thanks Tony, I thought it might be. Now I know.